Customer calls me back after I had rewired up and down sockets. The rcd trips when his bathroom underfloor heating (he installed) is left on for a while or straight away when thats on and the hoover is put on.
Go round, switch spur off, try hoover, works fine.
Measured the sensor resistance got 11ohms all ok. IR on heating matt. 250v. >99 L-E. 0 N-E. 31 L-N
Measured N-E on ohmmeter and got 103ohms
would you say the matt is damaged? and there is a short between N-E
Note MCB wasnt tripping Just RCD protecting that side of the cu was. Disconnected the matt and hoover would work fine no tripping.