Now I thought I new about RCD's and Earthing systems but cannot work this out.
Carrying out RCD testing with a tester that I know works on other DB's.
On this particular DB cannot get any RCD's to trip on 1x, 5x etc unless I connect the black and green leads swapped i.e. Black to E and Green to N.
Made me think that the supply to DB had reversal of N & E but cannot be as 2 core MICC from main switchroom, with sheath/metal frame as earth and the 2 conductors as L & N. Earthing arrangements TN-S.
The test button on each RCD does work.
I've tried another tester and the same happens, nothing, with standard lead connections, Red-L, Black-N, Green-E etc, but acceptable readings when N & E reversed.
Admittedly, I have not done any dead tests yet due to awaiting planned shutdown but cannot see that anything could be proved from that (polarity already checked - live testing), maybe continuity but the cable is complete from start to finish and never been altered.
Also there is another DB nearby in the same situation and fed from same DB in the main switchroom, but other DB's in the same building and fed from same main switch room ok when testing RCD's?
Any ideas
Carrying out RCD testing with a tester that I know works on other DB's.
On this particular DB cannot get any RCD's to trip on 1x, 5x etc unless I connect the black and green leads swapped i.e. Black to E and Green to N.
Made me think that the supply to DB had reversal of N & E but cannot be as 2 core MICC from main switchroom, with sheath/metal frame as earth and the 2 conductors as L & N. Earthing arrangements TN-S.
The test button on each RCD does work.
I've tried another tester and the same happens, nothing, with standard lead connections, Red-L, Black-N, Green-E etc, but acceptable readings when N & E reversed.
Admittedly, I have not done any dead tests yet due to awaiting planned shutdown but cannot see that anything could be proved from that (polarity already checked - live testing), maybe continuity but the cable is complete from start to finish and never been altered.
Also there is another DB nearby in the same situation and fed from same DB in the main switchroom, but other DB's in the same building and fed from same main switch room ok when testing RCD's?
Any ideas