Just wading through some plans and jotting down some circuit design notes.

Kitchen & Utility ring is probably going to be a mixture of Ref. method 102 & 103, stud walls full of cellotex. I reckon I'de sleep better if this was done in 4mm T&E. Am I being an old woman?

Oh and by the way, does cellotex affect sheathing the way them old poly balls does?

Cheers

Bez

 
Method 103 drops the rating of even 4mm to 17.5A. Ouch! Can't do a 32A ring on that. Couldn't even do a 20A radial on it.

I would suggest the careful use of noggins to ensure M102 throughout. 2.5 now has a rating of 21A, so you're able to do a 32A ring. 4mm has a rating of 27A so would be better for a 20A radial.

Personally I believe that a 20A radial is fine for most kitchen/utility uses. Most large appliances only pull full load during heating cycles for short periods. Only tumble driers pull full load for extended periods.

 
Method 103 drops the rating of even 4mm to 17.5A. Ouch! Can't do a 32A ring on that. Couldn't even do a 20A radial on it.
Doesn't that give you 35A when wired as a ring with 4mm though?

 