Today's job was a freebie for my daughter.
She is wanting some extra sockets in her lounge.
I decided to use my Fluke socket tester to verify which circuit to isolate.
The tester is showing 2 green and 1 red led illuminated. Eh?
Go to the board and do global insulation tests-- 4.5M ohms L-E, N-E and L/N-E.
I switch off all mcb's and the tester is now showing 1 red led.
Check all voltages coming in and they are ok. No voltage N-E.
It's a TT system (RA=12 ohms) and main switch is 30mA rcd.
Disconnect neutral and no led's are illuminated.
I rig a test socket direct from rcd out with earth connected to Ra and all bonding disconnected. All live and neutrals isolated
Same problem- 3 led's illuminated.
Rcd tests ok x1 and x5.
Socket tester works ok on neighbours sockets.
Your thoughts please.