Today's job was a freebie for my daughter.

She is wanting some extra sockets in her lounge.

I decided to use my Fluke socket tester to verify which circuit to isolate.

The tester is showing 2 green and 1 red led illuminated. Eh?

Go to the board and do global insulation tests-- 4.5M  ohms L-E, N-E and L/N-E.

I switch off all mcb's and the tester is now showing 1 red led.

Check all voltages coming in and they are ok. No voltage N-E.

It's a TT system (RA=12 ohms) and main switch is 30mA rcd.

Disconnect neutral and no led's are illuminated.

I rig a test socket direct from rcd out with earth connected to Ra and all bonding disconnected. All live and neutrals isolated

Same problem- 3 led's illuminated.

Rcd tests ok x1 and x5.

Socket tester works ok on neighbours sockets.

Your thoughts please.

 
I would have to guess that you didn't have 2 green and 1 red light showing.... I'm guessing that you only have 1 green and that the other is bleed through from the lit green.

So IMHO you have a L-N or L-E reverse,,, but then again I'd have proved it with a volt meter

but then again Canoey is probably right as I was looking at the SM100

 
Canoeboy said:
Does it not say on the tester what the LED code means ?

View attachment 6536


My one of those went mad, just tripped 30ma RCD's all the time & went in the bin.

I assumed it was all that bouncing about in my van that finally killed it off.

I do remember getting greens and a red but cannot recall the problem.

Found this though.



Have a kewtech one now & all is well.

:)

 
I found a unknown fault with mine last week , i think it was left red other 2 green & it turned out to be a missing neutral.
My one of those went mad, just tripped 30ma RCD's all the time & went in the bin.

I assumed it was all that bouncing about in my van that finally killed it off.

I do remember getting greens and a red but cannot recall the problem.

Found this though.


Have a kewtech one now & all is well.

:)
thats the thing some socket testers check for more things than others

 
I have trouble chucking things I payed money for :C

I did however chuck a load of old test leads away that I was hoarding just in case..."just incase what ? you break a test lead and your going to fix it with a broken test lead!?"  OFFS! 

just chuck it away but make sure it doesn't have one of those no throwy away symbols on it!

:slap

And my van resembles a well organised skip actually!

 