Any ideas on this one welcome...
Putting in the lighting circuit for this new kitchen. Pull a brand new wire from a lighting circuit MCB in the CU - have removed other circuit on same MCB to keep it simple.
Connectors are push fit Wagos in a Wagobox.
Have 2 existing (one way) wall switches and the loop cables are accessible wher they come out of the wall so using those.
Live comes from CU MCB to Wago, splits out into the two existing wall switches then come back in and connect to their respective load cables, the N's of which are connected to the N from the CU. Earths all connected back to CU (though no E in existing loop cables). All standard stuff... I assume.
So I rig up a temporary light to one cable and terminate the other with a choc block for testing. Power on.
First switch on = light on, switch off = light off.
Other switch on = 230v on cable, switch off = 48V ! (L-N & L-E)
So thinking there might be a leak through the switch, I pull off the switch plate and disconnect the wire - still 48V!!, disconnect wire to other switch, still 48V. Turn off everything else in the CU, still 48V. Remove the temporary light same problem there, though slightly less voltage.
Opened Wagobox and double checked everything and separated all the blocks - still 48v
MCB off= 0V
There is almost no current behind it (0.019ma) but it is an odd phenomena as as far as I can see it is coming off a disconnected wire!
Am I going insane? or is this a symptom of an average Multi Meter?
P.
Putting in the lighting circuit for this new kitchen. Pull a brand new wire from a lighting circuit MCB in the CU - have removed other circuit on same MCB to keep it simple.
Connectors are push fit Wagos in a Wagobox.
Have 2 existing (one way) wall switches and the loop cables are accessible wher they come out of the wall so using those.
Live comes from CU MCB to Wago, splits out into the two existing wall switches then come back in and connect to their respective load cables, the N's of which are connected to the N from the CU. Earths all connected back to CU (though no E in existing loop cables). All standard stuff... I assume.
So I rig up a temporary light to one cable and terminate the other with a choc block for testing. Power on.
First switch on = light on, switch off = light off.
Other switch on = 230v on cable, switch off = 48V ! (L-N & L-E)
So thinking there might be a leak through the switch, I pull off the switch plate and disconnect the wire - still 48V!!, disconnect wire to other switch, still 48V. Turn off everything else in the CU, still 48V. Remove the temporary light same problem there, though slightly less voltage.
Opened Wagobox and double checked everything and separated all the blocks - still 48v
MCB off= 0V
There is almost no current behind it (0.019ma) but it is an odd phenomena as as far as I can see it is coming off a disconnected wire!
Am I going insane? or is this a symptom of an average Multi Meter?
P.