the magic 1667 ohms
stringy
Oct 19, 2008
148
ive read on a few posts today about the magic 1667 ohms as somebody put it lol
im still learning the trade and could somebody please explain to me what its all about?
thanks matt
steptoe
Feb 13, 2008
24,337
117
Gtr Manchester
its about a reference to a max Zs to allow a maximum 50v touch voltage during fault conditions if you have a 30mA RCD for protection.
its actually a bit of a red herring now that 17th is here cos you are not supposed to use this method to calculate your disconnection times anymore, and the values would be slightly different anyhow being based on 230v now.
its still a good rule of thumb to work to tho.
stringy
Oct 19, 2008
148
arr right cheers steptoe
im kinda with you, so its a maximum zs value on any circuit? and earting system?
still confused lol
steptoe
Feb 13, 2008
24,337
117
Gtr Manchester
only if protected by a 30mA RCD.
but basically yes, you can use this as a reference to any circuit, although as it would be a deviation from BS7671 you would have to note this on the cert and also find/show an alternative way of proving your disconnection times are within BS7671-2008 guidelines.
sparkyork
Electrician
Oct 17, 2008
145
under certain condition and under certain applications of the 17th edition. to be fair i wouldnt be able to sleep at night if i left a socket circuit with a Zs of 1660 ohms say. what happens if the rcd fails? spesh if its a protek!! lol
steptoe
Feb 13, 2008
24,337
117
Gtr Manchester
would totally agree.
in all honesty stringy, unless you have a really good and total understanding of how to acheive your disconnection times AND stay legal when deviating from BS7671 then it is always advisable to stay within the regs and the quoted max Zs values.
stringy
Oct 19, 2008
148
thanks very much for the info guys, makes sense now
ive only been testing for a few months now but i have never got a zs reading that high.
thanks again
Nicky Tesla
Apr 30, 2008
1,638
I = V/R, R = V/R, 50v (max touch voltage)/0.03 (30mA) = 1666.6 ohms
the fact that we have moved from 240v to 230v does not make a difference here, cos max touch voltage is still 50v.
If there is a fault to earth on a piece of equipment, the voltage on that equipment will RISE from the original 0v upwards (this will take only fractions of a second). When this voltage has risen to 50v, if the resistance to earth on r2 is low enough, then at least 30mA will flow to earth and the RCD will trip in time. The voltage may rise still further than 50v but only due to the time it takes for the RCD to work.
Shakey
Oct 17, 2008
56
might be worth you reading the 'max Zs' thread, this is being discussed in depth there:D
stringy
Oct 19, 2008
148
ive been following it shakey, thinking to myself will i ever have that much knowledge haha :^O
GreekIslandLover
Oct 18, 2008
119
Pardon me for being wrong (I'm sure Shakey will hit me if I am!) but generally speaking, high Ze values are likely to happen mostly with TT systems. If you have TN or TNCS then you should (hopefully) have low Ze to start with, and therefore compliance with the maximum Zs of MCB's should be acheivable.
Shakey
Oct 17, 2008
56
absolutely correct GIL
and i stressed in the 'max Zs' post that the 1667 ohms figure should not be used as a 'get out clause' for poor design or installation:)