The right cert to be issued, whether minor works or EIC
Status
Not open for further replies.
pablobhinghi872
Mar 29, 2022
4
If you wire an alarm circuit into a CCU and then put it on the light circuit should this be a Minor Works Cert or an EIC as a new circuit that has been added into the CCU?
No it hasn't... by your own description you have connected onto the light circuit...
You have NOT added a new circuit to the CU..
(same number of MCB's / RCBO's were in the CU before and after you completed your alteration to the lighting circuit)
Go and read the definition of a circuit.. (Part 2 Bs7671)..
I think you will find it sates something about an assembly of electrical equipment supplied from the same origin and protected by the same overcurrent protective device...
Circuits ARE independent of each other... All equipment that becomes de-energised if your turn off the same MCB / RCBO is on the same circuit!
It is multiple final circuits it should be on its own protective device.
Why do you keep saying read Part 2. Each final circuit shall be connected to its own protective device, the alarm circuit is defined as a final circuit and no amount of 'read part 2' will alter that.
Sorry mate but you really have this wrong. If an OCPD has 2 cables in it, and its not a RFC, both cables form the circuit.
If you think we are all wrong please offer up your reference in the BB to clarify this.
Not at home to quote the Regulation but you say I am wrong then quote me the Regulation where it is acceptable to connect two final circuits to a single protective device.