Tinning Flex for Hob connection

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

gembrain

Active member
Joined
Dec 29, 2013
Messages
34
Reaction score
0
Location
Herts
So the new hob comes with a 5 core insulated flex. 2 cores together for live, 2 together for neutral, and one for earth. Only thing is they have taken off a silly amount of the outer insulation.

Sparky says soldered better than not and doesn't mention ferrules. So I cut off the nicely terminated ends, cut to the right length, strip and twist the two pairs and then out with the soldering iron and a bit of solder and they're fixed. 

Hunting for a decent connector block I come across a thread mentioning 526.8.2 .....

"Soldering (tinning) of the whole conductor end of multiwire, fine wire, and very fine wire conductors is not permitted if screw terminals are used"

I assume this is meaning the fixed installation rather than appliances and Sparky will clearly be happy to fit it with the tinned ends but should I get myself a crimper and do it "properly".

And why are tinned ends a problem with a screw terminal? 

Thanks :)

 
Hi there.

It is because lead is a material that "creeps" at room temperature. As you may have guessed, as the temperature rises, so does the rate of creep..

Have you ever looked at old lead pipes?? You will see that they have sagged down in between supports. They would not have been like that as installed. The material has "crept" with time under its own weight.

Anyway, in theory at least, the terminations are liable to slacken off with time..

Will the sparky care?? To be honest EVERY time i terminate stranded cables i use ferrules, BUT according to the factors where i get stuff, nobody else does.... In fact, to get uninsulated "bootlace" ferrules, i had to send away in the post, as the electrical factors do not stock them.....

Sparky will most likely not even be aware of the reg regarding this, but well done you!!!! I would get the ferrules though and do it properly. You will need the proper crimpers too

Ferrules https://www.rapidonline.com/truconnect-uninsulated-bootlace-ferrules-72043

Proper crimpers https://www.rapidonline.com/partex-bootlace-ferrule-crimping-tool-63944

P.S. Try and get a "selection box" [you know what i mean] of ferrules!! Another advantage while i think of it is it makes it easier to get cable strands in to the hole and there is the certainty of not having "stray" or broken off strands floating about... [Always a bad idea!!]

Hope this helps...

john..

 
Last edited by a moderator:
Thanks John and Andy - much appreciated :)

All makes sense and I will get the crimper and ferrules and do it proper!

 