Hi i am going to install a new air compressor. It suggests installing onto a 30 amp supply. I have a 30 amp supply.

The air compressor will be controlled by a float switch in a water tank which is about 60 meters away. The float switch is only rated at 10-15amp so my question is what can i use to connect the float switch to the compressor to turn it on and off?

Is there a contactor or a starter of some sort that i can wire in line for this?

The float switch is only a 2 wire switch so i think it used in line of the live wire. live goes in, through the float and back out to turn whatever on and off. Sorry if i have missed anything out.

 
A contactor would be used here. This would be fixed near the compressor with a smaller cable running to the switch. Have you checked the spec for the compressor , they have high start up current but drop to lower when running. You probably need a C curve breaker and an additonal smaller fuse/breaker for the control wiring. What is this project.

 
thanks for the fast reply.  I install well and borehole pumps but sometimes the well or borehole have very high iron or sand content so normal metal submersible pumps fail very quickly.

I have started using a new air driven pump with 1 moving part inside called a brumby pump. all plastic so does not corrode. Usually i only use a small compressor on a timer but this one requires a larger compressor and fills a large tank for irrigation.

From what i remember it is a 14amp motor. 

There is already a motor rated fuse installed and there is a 16amp standard fuse spur. Can i use the 16amp for the control?

Is there a specific contactor i need to get for this? I do not usually do the electrical side but as the breakers and fuse spurs/rotary isolators are already there all i need to do is wire into them plus it gives me a little more experience.

 
Given your situation, that you are doing this as a business and that you admit that you are unsure as to what you'd be doing, then I'd get someone in to do the elrctrical side as you have a duty to ensure that this is done safely and I doubt that you have the equipment to test your work

 
If you just turn the power on and off, there will be a delay as the compressor builds up to pressure, and when you turn it off, there will be a delay as the pressure runs down.  not very elegant.  then there's the issue of the stop start circuit, a non starter (literally) if the compressor has a no volt release.

So Is this a better suggestion:

Leave the compressor on all the time.  It's own controls will stop it when it gets up to pressure.

Use your flow switch to turn on a solenoid air valve, to supply air to the pump only when the flow switch calls for it.

Simple and elegant.

 
Prodave. you are an absolute legend. That is soo simple and elegant like your good self. Why did i not think of that! That has just saved a few £££ and a hell of a lot of hassle too.

a solinoid valve costs £30 and i work with them a lot of the time.

 