Volt drop
Traineeboy
Apr 22, 2020
201
17
Quick question on volt drop.
If you run power to an outbuilding ( single phase) when calculating volt drop would you allow the 5% for general or 3% for lighting. The outbuilding would have lighting in it but when I asked the question the chap I worked with he said you allow 5% as it’s not dedicated lighting it’s to a DB when it’s to lighting.
To me this doesn’t make sense where I would have thought it you are having lighting in the outbuilding you would only be allowed 3% as there is lights in there ?
Could I get some clarity please. Thanks Chaps.
As an unquoted rule of thumb 2% is often used for submains which allows for leeway on the final lighting and power circuit vd. Remember vd is based on the voltage at the source.
The 5%/3% is from the source of supply, as Fleeting has pointed out a good number to aim at for a submain is 2% but this isn't set in stone.
not heard that one before, albeit I have probbaly been doing this for years as I normally work out a cable size for the sub main, then up it one size to allow for 'changes of plan' .