john,Its the ratio of useful power compared to actual power, if the percentage is too low, then you can end up paying more for yur electricity. Local electrical supply companys insist on consumers using as high as possible power factor as possible and may insist on upgrades to your electricity supply. One way of improving is to use a capacitor. A low power factor can cause damage to your equipment and also can deteriate the cables as higher currents are in the cables.
Lol doesnt look like anyonme knows!Sorry to break up the domestic here guys!To steer the thread back on track...
Is Prospective Fault Current measured so the correct size (kA rating) breakers can be installed?
And that was a very funny reply!Main purpose is to check main protective device for installation ie DNOs fuse is capable of withstanding dead short circuit current, though in reality the likelyhood of dead short generating such an high ampage is unlikely unles it occurrs at 1mm from fuse so as to mimmise resistance. I did for many years believe that for example a 10K PFC would mean that 6K MCBs would not be suitable, this however is wrong ( I have discussed it my assessor) as again unless dead short occurs within CU (highly unlikely) they would never see min rersitance needed, and there are resistances down Meter tails and within main switch / busbars / MCB connections which are still sufficient to seriously drop ampage of dead short. Likewise if dead short happened 1mm from MCB, there is only that MCBs ampage going down circuit anyway. I shall now let argument commence for those that can be arsed to calculate numbers opcorn Sorry to drag thread back to question
Perhaps we should have a new section for threads that go seriously off topic, which is very amusing though also annoying when in a hurry ?:|
Not sure what 'ampage' is - but I can pretty much guarantee you that if you have a 'short circuit' at a distance of 1mm from any MCB, you will get pretty much the full 'PFC' flowing, not just the current flowing in that circuit.. Likewise if dead short happened 1mm from MCB, there is only that MCBs ampage going down circuit anyway.|
Falling asleep alreadyWhat Is The Purpose of Measuring PFC?So we can fill in the little box that says PFC of the certs!!!!!!
Yes
If you don't read it..
You can't fill it in!!!
Do they not teach younger training electricians to read books anymore...?
Try a bit of bedtime reading:-
Big Red BS7671
434.1 page 75 & 434.5.1, 434.5.2 page 76
Guidance note 3
2.7.16 page 52 through to page 54.
On Site Guide
7.2.7 page 56-57
and
10.3.7 page 88
Think those should help!
Guinness
You won't see them very often, anyway, because of the back-up protection provided by the cut-out fuse. - but I get your point.we don't see exploded MCBs very often. ray