Will be fitting a new boiler in a 1934 house in the next street to mine, all other houses TNS, checked CCU, new Wylex pop out Mcb's fitted 15-18 years ago 16mm bonding to services but noticed no main earth conductor connected to the incomer armour, looks like it has never been fitted ( no Marks on DNO SWA)
Whoever wired it has just left a 10" 16mm lead from the MET ready to connect to the SWA
Tested Ze on Met 0.08 ohms, pfc of 3.1KA, @ 248volts
Do I just call in EDF and let them sort it out,
I suppose they'll TNCS it if it has a high resistance on the Armour's Earth.
Many thanks All, Mike
Whoever wired it has just left a 10" 16mm lead from the MET ready to connect to the SWA
Tested Ze on Met 0.08 ohms, pfc of 3.1KA, @ 248volts
Do I just call in EDF and let them sort it out,
I suppose they'll TNCS it if it has a high resistance on the Armour's Earth.
Many thanks All, Mike