what type of earthing system is this?

Help Support Talk Electrician Forum:

dan.

Senior Member
Joined
Jun 17, 2008
Messages
274
Reaction score
0
on a job at the mo, over head power cables with a separate earth so 3 cables in total.is this a tns system or tt??

 

sirsparkabit

Well-known member
Joined
Mar 19, 2008
Messages
419
Reaction score
9
on a job at the mo, over head power cables with a separate earth so 3 cables in total.is this a tns system or tt??
More info dan please explain in detail what you have?

 

dan.

Senior Member
Joined
Jun 17, 2008
Messages
274
Reaction score
0
righto old converted farm house in ormskirk. over head power cables with 3 cables.3 uninsulated cables come down to the house are then insulated then go down the side wall and into the property.2 cables go into a normal type fuse the other which is the earth goes to an earth conection bar.

 

sirsparkabit

Well-known member
Joined
Mar 19, 2008
Messages
419
Reaction score
9
righto old converted farm house in ormskirk. over head power cables with 3 cables.3 uninsulated cables come down to the house are then insulated then go down the side wall and into the property.2 cables go into a normal type fuse the other which is the earth goes to an earth conection bar.
sorry mate i will leave this to the more suited who will be along soon no doubt:D

 

dan.

Senior Member
Joined
Jun 17, 2008
Messages
274
Reaction score
0
im pretty sure its a tns system but would like some comformation. just in case.

 

paulh

Senior Member
Joined
Jun 4, 2008
Messages
144
Reaction score
0
Like the Phone dno, If an earth is provided then it has to be a tn system doesn't it?

 

Admin1

Forum Founder
Joined
Feb 6, 2008
Messages
10,278
Reaction score
-1
Could it be an old TT that has been PME'd? :|

 

Admin1

Forum Founder
Joined
Feb 6, 2008
Messages
10,278
Reaction score
-1
Normally they are TN-C-S, Admittedly. But it is not uknown for a TT to be too.

 

steptoe

of course Im wrong, ask my wife™
Joined
Feb 13, 2008
Messages
24,337
Reaction score
117
Location
Gtr Manchester
more than likely TNS,

is it possible for you to trace the cable back to the transformer?

failing that, a loop test and PFC across all cables in turn will show up the likelihood of the different probabilities.

deffo NOT TNCS admin, the N E are NOT combined according to OP.

could be old TT where the pole is actually electrode,

wondering what type of trip is fitted now? is it an old voltage type????

could be an old TT without the earth, simply the incoming reference point for the trip.....

deffo needs a Ze ASAP methinks,,,

 

steptoe

of course Im wrong, ask my wife™
Joined
Feb 13, 2008
Messages
24,337
Reaction score
117
Location
Gtr Manchester
Normally they are TN-C-S, Admittedly. But it is not uknown for a TT to be too.
admin, you on the lemonade????? ; \

Terra Neutral Combined Seperate = IS = PME

Terra Terra = is simply what it says on the tin,

it canNOT be MULTIPLE EARTHed,

unless you count hammering more than 1 rod in, or you gonna put them in every 10metres back to the transfomer???? ?:| ? :|

 

Admin1

Forum Founder
Joined
Feb 6, 2008
Messages
10,278
Reaction score
-1
Yeah I know ** In Matt Lucas voice ** Can I export PME?

 

dan.

Senior Member
Joined
Jun 17, 2008
Messages
274
Reaction score
0
ze is coming in at 0.45 pfc is 550 so it looks like tns it is. Couldnt get in touch with dno.

 

steptoe

of course Im wrong, ask my wife™
Joined
Feb 13, 2008
Messages
24,337
Reaction score
117
Location
Gtr Manchester
ze is coming in at 0.45 pfc is 550 so it looks like tns it is. Couldnt get in touch with dno.
550kA ? or 0.550kA ?

what is that across? L N or L E ?

also can you do a loop test across L N too, give the ohm rating to centre point this way too, then can compare the PFC LN & LE and relate it to the centre point differential in ohms between Ln & LE.

thanks, sorry if it sounds a bit long winded but it does make a difference as to where your readings relate to at the transformer, ie, centre point or seperate Earth away from centre point.

(before you all start, I know centre point is Earth but in the interests of simplicity its easier to explain earth on TNS as being away(seperate) from centre point)

 

dan.

Senior Member
Joined
Jun 17, 2008
Messages
274
Reaction score
0
550amps not ka ,crikey that would blowthe house to bits.across L-N

 
Joined
Feb 27, 2008
Messages
11,034
Reaction score
0
righto old converted farm house in ormskirk. over head power cables with 3 cables.3 uninsulated cables come down to the house are then insulated then go down the side wall and into the property.2 cables go into a normal type fuse the other which is the earth goes to an earth conection bar.
I would not think it is tns on overhead as earth comes off armour on tns. Maybe originnally it had two phases and one of the phases has been changed to earth. A few pics would help.

Batty

 

dan.

Senior Member
Joined
Jun 17, 2008
Messages
274
Reaction score
0
ive got 1 pic of where the cables attach to the house but have nowhere to host it to get it on here.

 