andy_spark
Senior Member
[SIZE=medium]I have been asked to install some sockets in a scout hut, at a remote scout campsite, that is powered by a 6 kVA generator. There is currently a 2 way CU with 25A 30mA RCD main switch, feeding a 6A light circuit with about 6 lights on it and a 10A socket circuit feeding 1 outdoor socket.[/SIZE]
[SIZE=medium]The generator has an arrangement of 16A sockets 110v and 240v for outgoing supplies all protected by a 20A c type mcb double pole. The current cable is a 1.5mm flex running to the CU in a duct about 4 metres long about 6 inches under a path to the campsite hut. The generator itself is under a wooden shelter to keep rain off and the sides are half enclosed with covers. It is used mainly in the evenings to provide light to the hut which includes toilets a dining area and a kitchen. All cooking and water heating is gas with now plans to change.[/SIZE]
[SIZE=medium]The outdoor socket is in1mm and needs rewiring and about 4 new sockets to be added for using relatively low power kit ( phone chargers, radios, cleaning equipment and power tools etc). [/SIZE]
[SIZE=medium]I have not done a generator install like this before and have tried to understand it as best as possible form the books. I would appreciate any thoughts and comments or advice on my plan please.[/SIZE]
[SIZE=medium]My plan is to change the 10A to a 16A mcb for socket circuit and add new sockets, in 2.5mm T&E.[/SIZE]
[SIZE=medium]Fully test and inspect lighting circuit, it’s at least 15 years old[/SIZE]
[SIZE=medium]Install 10mm earth bonding to water supply which is in copper, connected to mains water (no bonding currently).[/SIZE]
[SIZE=medium]Rewire supply from genny to CU in 4mm SWA, (plenty adequate for 20A and also no plans to replace generator), it may not be possible to reach the CU with the SWA so the CU may have to be moved.[/SIZE]
[SIZE=medium]At genny end I will make off SWA in a IP66 box and finish the run to the genny in 4mm flex with IP66 16a socket, so it can be unplugged without stressing the SWA, unless anyone knows of a plug that SWA can be connected to.[/SIZE]
[SIZE=medium]Add an earth rod that will be connected to the earth lug on the generator.[/SIZE]
[SIZE=medium]Does an additional main earth from genny to CU need to be run in a larger size? I’m not that sure of the requirements of earthing so would grateful for any pointers.[/SIZE]
[SIZE=medium]The campsite managers understand the curernt install is not really up to scratch and there is a fair bit to do, budget is not infinite but funds are available to do it properly.[/SIZE]
[SIZE=medium]Thanks Andy.[/SIZE]
[SIZE=medium]The generator has an arrangement of 16A sockets 110v and 240v for outgoing supplies all protected by a 20A c type mcb double pole. The current cable is a 1.5mm flex running to the CU in a duct about 4 metres long about 6 inches under a path to the campsite hut. The generator itself is under a wooden shelter to keep rain off and the sides are half enclosed with covers. It is used mainly in the evenings to provide light to the hut which includes toilets a dining area and a kitchen. All cooking and water heating is gas with now plans to change.[/SIZE]
[SIZE=medium]The outdoor socket is in1mm and needs rewiring and about 4 new sockets to be added for using relatively low power kit ( phone chargers, radios, cleaning equipment and power tools etc). [/SIZE]
[SIZE=medium]I have not done a generator install like this before and have tried to understand it as best as possible form the books. I would appreciate any thoughts and comments or advice on my plan please.[/SIZE]
[SIZE=medium]My plan is to change the 10A to a 16A mcb for socket circuit and add new sockets, in 2.5mm T&E.[/SIZE]
[SIZE=medium]Fully test and inspect lighting circuit, it’s at least 15 years old[/SIZE]
[SIZE=medium]Install 10mm earth bonding to water supply which is in copper, connected to mains water (no bonding currently).[/SIZE]
[SIZE=medium]Rewire supply from genny to CU in 4mm SWA, (plenty adequate for 20A and also no plans to replace generator), it may not be possible to reach the CU with the SWA so the CU may have to be moved.[/SIZE]
[SIZE=medium]At genny end I will make off SWA in a IP66 box and finish the run to the genny in 4mm flex with IP66 16a socket, so it can be unplugged without stressing the SWA, unless anyone knows of a plug that SWA can be connected to.[/SIZE]
[SIZE=medium]Add an earth rod that will be connected to the earth lug on the generator.[/SIZE]
[SIZE=medium]Does an additional main earth from genny to CU need to be run in a larger size? I’m not that sure of the requirements of earthing so would grateful for any pointers.[/SIZE]
[SIZE=medium]The campsite managers understand the curernt install is not really up to scratch and there is a fair bit to do, budget is not infinite but funds are available to do it properly.[/SIZE]
[SIZE=medium]Thanks Andy.[/SIZE]