I am being brave posting this after reading all other posts on this subject so here goes.
Small workshop
20mtr run
Needs 4 S/O + 4 Five foot double florries.
13 amp welder, grinder hand tools ect to be used,(by one person!!)
House (small 2 bed) Has tncs system. Board has RCCB main switch so i will not be coming off spare way!.
My design is 20amp fused switched isolator fed from henley block
4mm 3 core swa to rcd garage unit with 16amp breaker to 2.5mm radial for sockets and 6amp mcb 1.0mm to lights.
I did talk this one over as originally i was going to tt the garage but after chatting to a learned friend he said if max Zs tables are not exceeded he did not see why the earth could not be Exported over this distance.
I do intend to contact local DNO for their views, of course all your views are respected and most welcome as usual.PrayPray