    • NozSpark
      NozSpark replied to the thread Would this be a C3 on next EICR.
      It’d only be a C2 if one of the circuits supplies a heater in the bathroom, or if the supply is TT,,,,, but only a C3 if supplying a...
    • NozSpark
      NozSpark replied to the thread Tysoft support problems.
      From what I’ve seen across several forums it seems like he’s so busy collecting his subscriptions that he hasn’t got much time to...
    • NozSpark
      You can’t I’m afraid, You’d need something like a Matt-e device fitting at the supply end of the cable.
    • NozSpark
      Yes it will, however none of those can protect you from O-pen faults
    • NozSpark
      Granny chargers don’t contain O-Pen protection 722 applies to all supplies for EV charging and requires a way to protect against O-Pen...
    • NozSpark
      OK,,, so you have the right idea with using a socket designed for EV charging,,, however you’ll also need an O-Pen protection device...
    • NozSpark
      NozSpark replied to the thread Help with specs!.
      Well you have said that you have installed 60m of 6.0mm SWA cable (in your opening paragraph),,,, that’ll allow for a load of upto 3.6kW...
    • NozSpark
      NozSpark replied to the thread Help with specs!.
      Personally i think that your submain is too small… with the volt drop you’ll be able to have a max of 3.6kW before you run into problems
    • NozSpark
      NozSpark replied to the thread MFT carry case.
      I have the Velocity 7.5 tester bag
    • NozSpark
      NozSpark replied to the thread Cooker tripping.
      Instead of asking your electrician to carry out a specific task, ask them to find and fix the fault… Ive had a fault on a lighting...
    • NozSpark
      NozSpark replied to the thread Earth leakage meter.
      I have a relatively cheap one and it’s help narrow down 2 fault today at a park lodge site… one was water in a wiska box for some trace...
    • NozSpark
      NozSpark replied to the thread EV charger fuse box tripping.
      The charge point in no way communicates with the GARO O-pen fault protection unit so the fault is more likely to be in that, personally...