The 100mA is a waste of money IMO. The safe touch voltage given by the big book is 50V. 50V/100mA=500 Ohms and you’ve got a Ra of over 500 Ohms. The RCBO’s are still providing the appropriate earth fault protection as 50V/30mA=1666.6 recurring. I would try extra rods and link them together to...
The 100mA is offering no discrimination at all. The RCBO’s are going to almost definitely be solid neutral so in the event of a neutral-earth fault the RCBO will trip, the neutral doesn’t disconnect so the 100mA RCD trips as well. Even changing it to a time delayed will result in the same...
Lol....I once had letter sent through from a company I was working for with a 1st class stamp on it stating I owed them 11 pence for private mileage :facepalm:
The draft for public comment was supposed to be released yesterday but due to technical issues it's been delayed to Monday......every one across the forums should get behind it and express our concerns if we agree somethings ridiculous.....just register on the IET site so you can read the draft...
I've just read this thread and sounds like complete guff....30 odd servers on a tin pot installation.....no UPS and no back up gen......The 600W load of each server resembles the load of a commonly used light used for cultivation.......If I were a betting man I would bet it's a ganja factory...
http://www.kentonline.co.uk/herne-bay/news/travellers-refuse-to-leave-car-124087/
http://www.kentonline.co.uk/herne-bay/news/travellers-enjoy-free-four-day-easter-124208/
Same thing near me
Your original design that the consultant is making you change sounds ****e anyway.....mcb's protecting distribution circuits that's going to have mcb's at the other end :Applaud