the DNO has quoted 25ka, we get 2ka further upstream
well,
as you run a successful electrical business, then you should know how to solve this,
go back to the DNO and ask for a measured PFC
the DNO has quoted 25ka, we get 2ka further upstream
Done this already waiting on the response.well,
as you run a successful electrical business, then you should know how to solve this,
go back to the DNO and ask for a measured PFC
Well it wouldn't beIt's been a long day, The consultants worry is the high falut current quoted be the DNO, however this isn't an issue further upstream
frm2005,Yes I did I was ******** you mum, thanks for *.*.*.* all
Are you taking the piss?
I know how the device works
I have run my own electrical company for 15 years.
The fault current noted on the device is what the device can safely cut agreed I have no issues with that.
My worry is that with a low falut current of less than 1ka in some instances would the mccb open.
School day, as they say,
I always thought that was the current it 'could' survive
As i understand, it the figures in the Ics column, are he current it can break and still be servicable [at least for a few times!!] and it WILL break the currents in the Icu column, but the device will now be stuffed...
john
View attachment 7985
My worry is that with a low falut current of less than 1ka in some instances would the mccb open.