25Ka at the intake 2ka is our calculated pfc at one of our bedsit consumer unit.
There's 4 blocks
A,B,C,D
block C is where the intake is the substation is on site 8 meters away from our main LV panel situated in block C. This is where we'd see the highest fault current obviously.
block A is 100m away from our LV panel we are feeding Block A (which requires a 400amp supply) with 2x 240mm 4core cables wired in parallel. This is why there is such a drop in pfc, the apartment DB is about 30m away from block a's panel the bedsit dB is another 20m away from that.
This is why we don't believe a mccb rated at 25ka fault current is required that far upstream.
There's 4 blocks
A,B,C,D
block C is where the intake is the substation is on site 8 meters away from our main LV panel situated in block C. This is where we'd see the highest fault current obviously.
block A is 100m away from our LV panel we are feeding Block A (which requires a 400amp supply) with 2x 240mm 4core cables wired in parallel. This is why there is such a drop in pfc, the apartment DB is about 30m away from block a's panel the bedsit dB is another 20m away from that.
This is why we don't believe a mccb rated at 25ka fault current is required that far upstream.