  1. mushka

    CU change found IR fault

    They're still there just in wagos. Still acceptable? or should I start hacking?
  2. mushka

    CU change found IR fault

    ok, that'll do for me for the time being untill I've got a day when the mrs + kids will be out and I can sort it. cheers
  3. mushka

    CU change found IR fault

    I'm still confused by the apparent dead short and the fact that I'm getting 0.32Mohms between L-CPC and also between N-CPC And that 0.32 is just that for both live conductors to earth!! Maybe I'm just missing something?
  4. mushka

    CU change found IR fault

    yeah ring tested fine, in fact I got really nice results, it was only when I got to IR testing did the poo hit the fan
  5. mushka

    CU change found IR fault

    I think someone might have put a screw through a cable as I've pulled up some carpet seen a bunch of boards just wapped down with 2inch screws.
  6. mushka

    CU change found IR fault

    That's what I thought but having disconnected this one section it's all fine and dandy! (although no longer a ring!) I actually measured the resistance at 450Ohms on continuity, so it's only allowing about .5A to flow. Do you still think it could be something else on the circuit? cheers
  7. mushka

    CU change found IR fault

    Evening fellas, I've just changed a CU (in my house for NICEIC major job) and after 2 days of trying in vain to find some load I'd forgotten to remove from the upstairs ring, I came to the conclusion that my results for Insulation resistance for the circuit of L-N = 0.00M ohms and L-CPC =...
  8. mushka

    non cert, certs (are 'logo headed certificates required?)

    ****BUMP***** MODERATOR PLEASE MAKE THIS STICKY!! really well put description of how all this certification stuff works. brilliant! Guinness for you mate!