  1. L

    Ten things unheard of when I grew up .

    I think they were correct with what they’ve told you about the insurance. car traders/dealers do it all the time as they have a selection of stock to choose from and use the vehicle because they have a traders policy. 
  2. L

    TT System

    The 100mA is a waste of money IMO. The safe touch voltage given by the big book is 50V. 50V/100mA=500 Ohms and you’ve got a Ra of over 500 Ohms. The RCBO’s are still providing the appropriate earth fault protection as 50V/30mA=1666.6 recurring. I would try extra rods and link them together to...
  3. L

    TT System

    The 100mA is offering no discrimination at all. The RCBO’s are going to almost definitely be solid neutral so in the event of a neutral-earth fault the RCBO will trip, the neutral doesn’t disconnect so the 100mA RCD trips as well. Even changing it to a time delayed will result in the same...
  4. L

    TT System

    Are the RCBO’s SPSN/double pole?  Is the upfront RCD time delayed? 
  5. L

    television...

    Lol....I once had letter sent through from a company I was working for with a 1st class stamp on it stating I owed them 11 pence for private mileage  :facepalm:
  6. L

    At which point did this seem a good idea!

    ^^^^The UK's friendliest electrical forum at its finest.........
  7. L

    spot the fault™

    This is the sort of ****e we are pricing against.....
  8. L

    17th ....18th edition Regs ?

    The draft for public comment was supposed to be released yesterday but due to technical issues it's been delayed to Monday......every one across the forums should get behind it and express our concerns if we agree somethings ridiculous.....just register on the IET site so you can read the draft...
  9. L

    Need some advice on new server room

    I've just read this thread and sounds like complete guff....30 odd servers on a tin pot installation.....no UPS and no back up gen......The 600W load of each server resembles the load of a commonly used light used for cultivation.......If I were a betting man I would bet it's a ganja factory...
  10. L

    Lighting problem

    You have no neutral. Switch the circuit off and call an electrician.
  11. L

    Ah the romance of the open road and the Travelling People.

    http://www.kentonline.co.uk/herne-bay/news/travellers-refuse-to-leave-car-124087/ http://www.kentonline.co.uk/herne-bay/news/travellers-enjoy-free-four-day-easter-124208/ Same thing near me
  12. L

    My new toy

    err yes they do.......the majority of cases the CPS deal with go to magistrates.
  13. L

    My new toy

    haha agreed :facepalm:
  14. L

    My new toy

    Must be well chuffed with yourself.......... :Applaud
  15. L

    MCCB

    Your original design that the consultant is making you change sounds ****e anyway.....mcb's protecting distribution circuits that's going to have mcb's at the other end  :Applaud
  16. L

    Another load of carp in today

    As its over 7 years he will have to do at least 2/3 of the sentence not half.
  17. L

    It seems to be the name of the game these days!

    Lovely place Shrewsbury...Lived there until I was about 10 then moved to Kent. I used to visit at least once a year but haven't been back in about 5 years now...should make the effort really.
  18. L

    Thermostat upgrade connection

    Sounds like you have a two port valve on the flow as it enters the property. 
  19. L

    Alarm with proximity fob

    Another 1 for texecom premier elite.
  20. L

    Distribution Circuit on DNO fuses.

    https://www.meteroperators.org.uk/stakeholder-info https://www.dcusa.co.uk/Documents/Panel _043 11 Electricity Metering FAQ Doc.pdf#search=length of meter tails The Distribution Connection and Use of System Agreement (DCUSA) is as a multi-party contract between the licensed electricity...
Top