  1. S

    Irony

    Good point
  2. S

    Irony

    We go to length by design to ensure shock protection. Zs must be measured and be below a certain figure. If the user is working at the end of a 30 Metre extension, he is risking a shock if a fault to earth occurs while using an earthed metal tool. The disconnection time will exceed 0.4 sec...
  3. S

    DIY strikes again

    With your reply in mind, a spur from a ring should only feed one single or twin 13Amp socket. There are two in this case, but no matter how you argue, it is a dedicated cooker final circuit, and I observed it while investigating why the lower oven was not heating. I was NOT doing an inspection...
  4. S

    DIY strikes again

    Inspection of a domestic kitchen showed that two twin 13A sockets were spurred off the cooker outlet. Cooker exists fed from cooker outlet as well. What C rating do you give? What to say/report to customer?
  5. S

    How do you fix this?

    During an inspection it was observed that twin flush sockets were installed on a finished engineering brick wall. The installer had simply left a half brick space for each socket resulting in no proper landing for the over-sized space. How would you remedy this?
  6. S

    Presence Switching

    I understand. Thank you.
  7. S

    Presence Switching

    I am having trouble getting the Thea Microwave sensor to calibrate properly for movement of a human walking below it. It is loosely fitted inside a 5ft twin led batten, corrosive type by Ansell. The leds are fitted to a steel tray inside the luminaire and when up in a single garage rafters...
  8. S

    Tools Explained

    Turned out that it was the armature from a large motor which weight a few cwts and needed a wheel barrow to shift from the armature winding dept to the stores where I worked at 15.
  9. S

    Tools Explained

    Was sent for a 3ft ASTRALISER
  10. S

    Movement switching of groups of luminaires.

    Thanks for that info and advice. What is the diff between these sensors and the micro sensors that can be installed inside a luminaire?
  11. S

    Movement switching of groups of luminaires.

    That is the point, the normal switch control would be unable to over-ride the sensor. would connecting the floating contacts of the sensor in parallel across the line and switch-wire During a meeting the room would be plunged into darkness after the sensor timed out. I can't see how this would...
  12. S

    Movement switching of groups of luminaires.

    Been asked if I could install a PIR detector to bring on luminaires in a meeting room which has two way switching. I have seen this in new builds but this is an existing build. What happens when there is a meeting taking place and movement ceases. How is this arranged and what materials are...
  13. S

    Commercial Dishwasher

    Just wanted verification - thank you.
  14. S

    Commercial Dishwasher

    My church has taken delivery of a 4.4kW commercial dish washer.  They are assuming it can be powered from the ring final circuit in the kitchen or from the boiler circuit. Am I correct in saying that this is "not on".  Should it not be wired back to the Dist Board?
  15. S

    What should I do?

    Many thanks for your reply
  16. S

    What should I do?

    Many thanks for your reply Thanks for this reply. Appreciated.
  17. S

    Does anyone know what the following means ?

    I'm a sparkie and a computer techie.  If you give me a personal message I can chat about it and should be able to help. Says-Les
  18. S

    What should I do?

    I'm a retired spark who taught the 14th,15th and 16th editions to apprentices and to sparks updating their knowledge base/qualification.  I am self taught by studying since an apprentice, have gained C & G Full Tech Certificate back in the 60's.  I still read up and have a copy of the 18th...