    How to, Underground cable joint

    Youd be quite surprised. Minus the armour bond it is pretty much the same for a service cable joint. On another note, that constant force spring is the same method how the earth screen is connected to on 11kv and 33kv cables.
  2. D

    How to, Underground cable joint

    Taping or patch is useful if you have to do one live! Also don't need a collar as the resin will go hard and prevent the armours from digging in
  3. D

    Why are main bonding conductors so big?

    It seems PNB systems are open to interpretation. Even the wiring regs book says that a TNS systems can be considered to be TNCS PNB
  4. D

    Why are main bonding conductors so big?

    Have heard of pnb but dont have much dealing wih is as I work U/G, its where the N/E is provided from a point away from the transformer and the premises? Will hold my hands up if that can be classed as tnc-s. But have always been told that for an installation to be given tnc-s it has to be pme...
  5. D

    Why are main bonding conductors so big?

    Then without that multiple earthing it cant be TNC-S as stipulated by the regs. Thats not to say there is an incorrect sticker on an installation. ---------- Post Auto-Merged at 20:58 ---------- Previous post was made at 20:57 ---------- Each joint where the two are bonded an earth tail is sent...
  6. D

    Why are main bonding conductors so big?

    my bad, its shall Protective multiple earthing 9.
  7. D

    Why are main bonding conductors so big?

    Just thought of the exception, swimming pools and petrol stations when there is no separate earth and you have to provide your own. PME supply with tt earthing
  8. D

    Why are main bonding conductors so big?

    On a modern combined neutral earth mains cable, TNC-s supply, each joint along the main has an earth tail coming out of it tying the neutral to earth. Thus PME and tncs. If the original mains cable was separate neutral earth and was converted to pme, joints along that cable will have the...
  9. D

    Why are main bonding conductors so big?

    Am guessing your thinking of an old PILC supply into a property where a modern cutout has been fitted to it?
  10. D

    Why are main bonding conductors so big?

    The bonded earth conductor has to be of a sufficient csa to carry the fault current long enough to trip the main C/O fuse of a fault in the event of the shared N/E not present. Too small a conductor will not provide a sufficent fault current to trip the overcurrent protection. BTW PME and TNC-S...
  11. D

    Mains Jointing

    They're shear off connectors again but you have strip the insulation
  12. D

    Mains Jointing

    Dont wipe joints any more, its all done with mechanical connectors now. The connector on the the top of the joint on the 3rd pic is a shear off connector for the earth screen on a 33kv transition pilcswa to triplex. Just tighten them up with a ratchet and they shear at a pre set torque.
  13. D

    Mains Jointing

    Haha, just a couple. Had my lv 2 2339 exams today which was fun!
  14. D

    Mains Jointing

    Yeah am an apprentice jointer and took em down the training school. The rigs are live simulators that sound an alarm if you go phase to phase or phase to neutral
  15. D

    Mains Jointing

    Some assorted pics. 33KV jointing, lightening vs a street lighting C/O 185 wavecon to 185 PILCSTA breach joint and a 185 wavecon srevice breach