    4 Pole Rcd On Sports Lighting !help!

    Was meant to say here are the pics... The lamps are a good 25-30 feet up so I'm just going by the spec I was given. They are abut 18 months old and the problem started about 4 months ago. It could be failed control gear but all the lights work and none appear to be failing. It's a dilemma I just...
  2. L

    4 Pole Rcd On Sports Lighting !help!

    Here http://i1353.photobucket.com/albums/q679/lukewhiting69/image_zps42d5e699.jpg http://i1353.photobucket.com/albums/q679/lukewhiting69/image_zpsce41a584.jpg http://i1353.photobucket.com/albums/q679/lukewhiting69/image_zpscbbab369.jpg...
  3. L

    4 Pole Rcd On Sports Lighting !help!

    I have got some pics i will post them in a bit and show u all the arrangement
  4. L

    4 Pole Rcd On Sports Lighting !help!

    63A 30mA and they trip at 25mA 1x 42mS 5x 14.8mS
  5. L

    Ugly Wife

    Ha that's quality
  6. L

    New To This Forum

    Hi I'm Luke and I'm new Hi I'm Luke and I'm new Hi I'm Luke and I'm new
  7. L

    4 Pole Rcd On Sports Lighting !help!

    Apparently the lights are a year old. They changed all the stantions and fittings and switchgear but left existing RCD and cabling to the lighting.
  8. L

    4 Pole Rcd On Sports Lighting !help!

    They are all fine at 1stni thought RCD might be on its way out but all fine
  9. L

    4 Pole Rcd On Sports Lighting !help!

    I think I have some pics hold on guys ... Done an IR batty and all came back fine even blasted 1000v down it
  10. L

    4 Pole Rcd On Sports Lighting !help!

    You got 2 cables per phase coming off the load side of the RCD, they go to there designated terminal on each isolator. So basically u got one side of the pitch (3 poles-9 lamps) on one isolator and one side on the other. 3ph up each pole and obviously each fitting is 230v. It's wired as a...
  11. L

    4 Pole Rcd On Sports Lighting !help!

    Hi I have been asked to look at the lighting at my local sports centre. I been to look and the set up is as follows. 3ph supply TN-C-S to a 4 pole 63A RCD, This feeds two isolators that each feed 3 stantions either side of e pitch. The lights are 3x 2KW high pressure sodium lamps per stantion...