Went to an RCD tripping randomly today, kitchen was showing 0.1meg L+N to E. located it to a dishwasher. Would this be enough to trip the RCD? I imagine with it being so low anything else slightly adding to the leakage will make it trip?

Tom

 
Well,,,,

I=V/R

=230/1000

=0.23A. or 230mA

So yes, easily enough to trip a 30mA RCD

EDIT......

oops, 0.1M = 100000 ohms not 1000 ohms... doh

So as said by others below its only 2.3mA, and by itself shouldn't trip a RCD

 
Amazing, those basic calculations you learn on day one of any training about anything electrical are useful, fancy that.

 
Erm isnt that 230/100000? so 0.0023A or 2.3mA?

I assume you tested on IR setting? 0.1Mohm may not be accurate on that scale so could be lower still.

 
Perhaps he did remember ohms law, used the correct figures and determined that a 30mA RCD should not trip at 2.3mA.

 
Went to an RCD tripping randomly today, kitchen was showing 0.1meg L+N to E. located it to a dishwasher. Would this be enough to trip the RCD? I imagine with it being so low anything else slightly adding to the leakage will make it trip?Tom
if your getting a reading that low, change setting to continuity. sometimes a bit more useful

 
can you test the rcd.... and see if its over sensitive???

could be tripping at 15mA?

I only say this, as early this year I had a similar issue regarding RCD and a dishwasher.

tested the RCD on ramp test (15mA),

 