Something not right there, you lost your calculator?20 amp oven and 45 amp hob, and socket am i right in thinking 31.5 amps or is it 34.5 amps
its a bit lateSomething not right there, you lost your calculator?
Just to confirm for any others reading where some of these calcy bits come from....20 amp oven and 45 amp hob, and socket am i right in thinking 31.5 amps or is it 34.5 ampsand is it ok off 1 switch or do they both need isolating
Well thats a helpful and informative statement? :|Something not right there, you lost your calculator?
Many thanks for explaining that in plain english, I sort of knew already but it's nice to see it confirmed, and also the more times you read these things, the more they stick.Just to confirm for any others reading where some of these calcy bits come from....Page 160 On Site Guide. Appendix 8
8.4 Cooker circuits in household & similar premises
general comment:
a 30 or 32 amp circuit is usually appropriate for household or similar cookers up to a rating of 15kW
20A + 45A = 65A x 230v = 14950watts (upto 15kW )
OR Diversity calcs:-
Appendix 1 Page 96 On Site Guide.
First 10A
+ 30% of remainder
+ 5A if a socket outlet included.
so 10A + (0.3 x 55A) + 5A = 31.5Amps
so 26.5 if no socket, 31.5 with socket.
Switching:-
The guidance on Page 160 states a circuit between 15A and 50A may supply TWO or MORE cooking appliances providing they are in the same room.
One switch can supply two appliances providing its is no more than 2m form both appliances.
Very un-informative postApplaud SmileySomething not right there, you lost your calculator?
Cheers.Well thats a helpful and informative statement? :| I am so pleased to be in your presence oh wonderful wise one..Pray
We are NOT worthy................................
Incorrect info!Yeah, I worked that out earlier, last night it made no sense!As for the isolation, I would always isolate each device individually. I'm fairly certain it says as much in the regs somewhere, good practice anyway. If you use the existing cooker control then I'd add 2 isolators in an adjacent cupboard.
Can't see problem with that no different to having one cooker only time may switch them separately if it was a really high current being drawn.Incorrect info!try Page 160 one site guide....
(which complies with Regs & is good practice! )
One switch can supply two appliances providing its is no more than 2m form both appliances.
Fair enough. I'd still isolate each one individually though.One switch can supply two appliances providing its is no more than 2m form both appliances.
Fair enough. I'd still isolate each one individually though.