Hi,
An earth fault loop impedance test on a 50A compressor circuit gives a result of 0.93 ohms. The result of the previous cpc continuity test for this circuit gives (R1+R2) as 0.47 ohms. The ambient temperature at the time of test was 25 degrees celcius (factor 0.98) and the cable is 70 degree pvc (factor 1.2). If the maximum tabulated value of Zs for this circuit is 1.09 ohms, show by calculation (not rule of thumb method) if the measured value of Zs is accepable.
Thanks for any replies
An earth fault loop impedance test on a 50A compressor circuit gives a result of 0.93 ohms. The result of the previous cpc continuity test for this circuit gives (R1+R2) as 0.47 ohms. The ambient temperature at the time of test was 25 degrees celcius (factor 0.98) and the cable is 70 degree pvc (factor 1.2). If the maximum tabulated value of Zs for this circuit is 1.09 ohms, show by calculation (not rule of thumb method) if the measured value of Zs is accepable.