2391
quick edit by andy lol
got myself a little confused...
166 ohms is the max Zs for 300mA. but under TT, isnt fault protection now 30mA? im looking through regs now trying to find answer
dont really see what Ra of 166 had to do with it?
Fire protection should be 300mA max RCD (532.1)
got myself a little confused...166 ohms is the max Zs for 300mA. but under TT, isnt fault protection now 30mA? im looking through regs now trying to find answer
i'm not 100% but think the main switch would need to be 100ma to cover nuisance
unfortunately, with RCD's it can be very hard to provide discrimination. unless one is a TD, a fault can easily trip both. but you may not be able to use a TD
true but you will have satisfied the regulation by fitting it
i cant find my 17th osg, is there any problem with using my old 1 for reference in the practical . ????
not much has changed really its just for tables etc ..
I don't think nuisance tripping and discrimination are the same thing!
neither do i!
i disagree but i'm hoping to be enlightened
its a nuisance if a fault on a circuit takes out its protective device and a device further down stream (discrimination) so they go hand in hand wouldn't you say
isnt nuisance under normal conditions and discrimination incase of fault. so fault tripping would be lack of discrimination. nuisance would be too many computers on 1 RCD with high earth leakage
No - that's supposed to happen! It's a nuisance when a fault on one circuit knocks out another (eg fault on ring - you loose the lights, fall down stairs looking for CU)
to the letter Applaud Smiley
thats what i wrote ROTFWL
it is a nuisance, but its because of a fault and lack of discrimination!