Hi all, new here.
Just trying to sort out a problem for the mrs. So all or any help would be greatly appreciated
The mrs. has been trying to convert a minibus into an ice cream van. We are now at the stage where we need to power the ice cream machine. We are trying to use a generator for this.
Here we go: On wash/rinse cycle the generator runs fine switch the machine to run the mix through and the breaker on the generator is tripped straight away. And we cant seem to get past this point. I will now supply the specs of both machine & generator so please any help would be great, thanx.
The Machine: Taylor Freezemaster 320-44
240v
Min amp 17
Max amp 20
Phase 1
Other motor amp 7
Cy 50
Compressor 7.5 RLA
Beater 6.1 FLA
60.0 LRA
This is all the info i can find on the machine.
The Genny. Loncin 6500DDC 6.5 KVA Petrol
Rated voltage 115/230v
Rated frequency 50Hz
Rated output 5.0Kw
Maximum output 5.5Kw
Power factor 1.0
Many thanx in advance Taxidriver
Just trying to sort out a problem for the mrs. So all or any help would be greatly appreciated
The mrs. has been trying to convert a minibus into an ice cream van. We are now at the stage where we need to power the ice cream machine. We are trying to use a generator for this.
Here we go: On wash/rinse cycle the generator runs fine switch the machine to run the mix through and the breaker on the generator is tripped straight away. And we cant seem to get past this point. I will now supply the specs of both machine & generator so please any help would be great, thanx.
The Machine: Taylor Freezemaster 320-44
240v
Min amp 17
Max amp 20
Phase 1
Other motor amp 7
Cy 50
Compressor 7.5 RLA
Beater 6.1 FLA
60.0 LRA
This is all the info i can find on the machine.
The Genny. Loncin 6500DDC 6.5 KVA Petrol
Rated voltage 115/230v
Rated frequency 50Hz
Rated output 5.0Kw
Maximum output 5.5Kw
Power factor 1.0
Many thanx in advance Taxidriver