HI Ryanm,
Just to try to rephrase what has been said in more "laymans" terms, [i am a layman so would know!!]
First, the three contactors...
If you look in the terminal box of a motor, you will find 6 terminals [usually] Imagine that you connect the three incoming phases to the one row of three terminals, say the top row. If you connect the little brass links across to the other three, you have just wired the motor in "delta" and the motor will need 400V.
If instead you connected the three incoming phases to the one row of three terminals, but then just linked the "other" three to each other, [instead of to the "first" three] you have connected the motor in "star" What you have done, is you have connected the "mains" to one end of all three windings, and by linking the "other" row of terminals together, you have formed the "star point" if you follow me.
Best way to see it is; The first contactor, the "line" contactor, powers the whole lot up, and as Sidewinder has said, it connects the incoming power to one end of all three windings, one phase to EACH of the separate windings.
The "Star" contactor closes at the same time, and connects the "other" three ends of the windings together [just like you could with the "links" in the terminal box] to form the "star point", so the motor starts in star. Then after a time preset with a timer, the "star" contactor opens, and the "Delta" one closes and quickly reconnects the motor in "Delta" instead, [again, just like you could with the links in the terminal box] so that the motor keeps on running.
Idea is, in delta the motor runs on 400v yes?? In star though, it would need more like 690V.... So why would you do that???? Well, by wiring the motor so it needs 690V [but only giving it 400v] you have greatly reduced the power of the thing, this means that it will start a lot more gently and avoid a sudden, violent start that might damage the machine it is connected to, and also, just as importantly, it vastly reduces the starting current needed by the motor. In practice, all motors above about 7.5hp are started "star/delta" to avoid the high current demands that would other wise be needed if you just switched them on, "DOL" [direct on line]
Once the motor is running, the timer then swaps the two contactors, opening one [disconnecting the "star" wiring] and closing the other [connecting the delta wiring], so now the motor runs in "delta" on its "proper" voltage, and develops full power..
Here is a link to a diagram of how the thing would be wired so you can visualise it all.
http://i1178.photobucket.com/albums/x373/resistance87/stardelta.jpg
john...
Look carefully at the diagram... Can you see that the "star" and "delta" contactors are just doing exactly what you could do yourself by changing the links in the terminal box??? They just do it more quickly than you could !!!!!
john...