Had a little job today, installing Class 1 light fitting at a mid 60s built dwelling, no CPC on lighting circuits.
Ran a 4mm 6491x from C Unit to the new light fitting, proved continuity with wander lead R2, but then on doing a polarity check found it was reversed. Checked at other light fittings to find the same. The circuit was wired in singles L looped at switches, N at Light fittings, except that at first switch I found 2 Reds and a Black and at first Light 2 Reds and 1 black.
So what had the original sparky done here in 1965?
Ran a 4mm 6491x from C Unit to the new light fitting, proved continuity with wander lead R2, but then on doing a polarity check found it was reversed. Checked at other light fittings to find the same. The circuit was wired in singles L looped at switches, N at Light fittings, except that at first switch I found 2 Reds and a Black and at first Light 2 Reds and 1 black.