Hello,
I am looking for help and advise with a summation supply arrangement.-
I have been asked to quote to install a supply to a shed (yes it is that time of year again!), where the intended additional load is (60-70A).
Combine that (60-70A) with the existing demand of the house including diversity of 105A, it would seem (on paper at least) to much for a single phase supply. I havent checked the main fuse, but it says 60A on ceramic holder.
Ive been considering suggesting to the customer to have 3 phase installed, but then it opens up problems with balancing the load between phases etc etc, and all the expense.
Would it be reasonable in this case to suggest a summation supply? I am asuming the supply company can (at cost) install a second fuse head from the same single phase supply.
Has anyone here done this or had to have this done?
Any idea of costs?
All help or advise welcome.
Many thanks.
I am looking for help and advise with a summation supply arrangement.-
I have been asked to quote to install a supply to a shed (yes it is that time of year again!), where the intended additional load is (60-70A).
Combine that (60-70A) with the existing demand of the house including diversity of 105A, it would seem (on paper at least) to much for a single phase supply. I havent checked the main fuse, but it says 60A on ceramic holder.
Ive been considering suggesting to the customer to have 3 phase installed, but then it opens up problems with balancing the load between phases etc etc, and all the expense.
Would it be reasonable in this case to suggest a summation supply? I am asuming the supply company can (at cost) install a second fuse head from the same single phase supply.
Has anyone here done this or had to have this done?
Any idea of costs?
All help or advise welcome.
Many thanks.