After sorting the major job for my Elecsa assessment my neighbour has asked if I can fit a additional socket to his garage. Good timing!! But... here`s the dilemna:
We all do our work to the best of our abilities and compliant to the current Regs but been assessed by a scheme provider is obviously a time where every t is crossed and i dotted!!
My neighbour has in the kitchen, not one old Wylex board but three and it looks like many ways are supplying just one socket outlet each?? I think there are two 8-way and one 6-way. I know this is not directly relevant to the garage socket but trying to build a picture .
From one of these 8-way boards a 30A fused way supplies (via 6mm T&E) a 2-way wylex board in the garage with:
30A fuse that covers the garage ring (just 3 socket outlets)
6A fuse that covers the lighting for the garage.
My intention is to spur off a socket in the garage and fit a metal-clad double socket outlet on the opposite wall. The cable will be clipped-direct up the wall, along the ceiling and down the other wall.
My query is this: I have worked on/altered the circuit so should be RCD protecting. However, because the cable is surface mounted, RCD protection is not required.
But it`s a garage.....socket outlets.....garden power tools. Ok, but when I fit a garage enclosure and the lights and sockets become RCD protected I have effectively worked on the supply to that distribution circuit and should therefore be RCD protecting from the kitchen CU also. RCBO for the old Wylex board?? Surely not.
Have I missed something obvious here?? (Yet to check the bonding) All comments definately welcome
Constructively critical or otherwise Blushing
thanks in advance, Craig
We all do our work to the best of our abilities and compliant to the current Regs but been assessed by a scheme provider is obviously a time where every t is crossed and i dotted!!
My neighbour has in the kitchen, not one old Wylex board but three and it looks like many ways are supplying just one socket outlet each?? I think there are two 8-way and one 6-way. I know this is not directly relevant to the garage socket but trying to build a picture .
From one of these 8-way boards a 30A fused way supplies (via 6mm T&E) a 2-way wylex board in the garage with:
30A fuse that covers the garage ring (just 3 socket outlets)
6A fuse that covers the lighting for the garage.
My intention is to spur off a socket in the garage and fit a metal-clad double socket outlet on the opposite wall. The cable will be clipped-direct up the wall, along the ceiling and down the other wall.
My query is this: I have worked on/altered the circuit so should be RCD protecting. However, because the cable is surface mounted, RCD protection is not required.
But it`s a garage.....socket outlets.....garden power tools. Ok, but when I fit a garage enclosure and the lights and sockets become RCD protected I have effectively worked on the supply to that distribution circuit and should therefore be RCD protecting from the kitchen CU also. RCBO for the old Wylex board?? Surely not.
Have I missed something obvious here?? (Yet to check the bonding) All comments definately welcome
Constructively critical or otherwise Blushing
thanks in advance, Craig