Hi all, Now i am only a beginner at all this, so please do not all shoot me down and might all criticism be constructive please!!!!
Sooooo, here we go!!!
For a 32 amp type B mcb on 230V the MAX Zs is 230 / 32 x 5 = 1.437 ohms
Now, i have a copy here of an NICEIC eic form, and, sure enough, the question is "Maximum Zs as permitted by BS 7671"
So, the correct answer to the question as written, is definitely, no matter what, 1.437 ohms
Now then, this refers to the maximum Zs in actual service conditions, in other words, at the operating temperature of the conductors, [which we all know increases with temperature]
When you are designing a circuit, the figures you will find in the various charts for the resistivity of the conductors are all given at the standard temperature of 20C.
So the calculation you would do would be something like;
The length of run of the cable, x [R1 + R2] x around 1.2 [to correct things to allow for the fact that the conductors will be assumed to be at 70C in use instead of 20C] all divided by 1000 to convert from milliohms to ohms.
When you are verifying an installation on site, it is assumed that everything will be all cooled down and back at ambient temperature. So we need to "reverse" the original x 1.2 bit that we did in our design calcs. The reciprocal of 1.2 just happens to be about .8 !! Sooooooo, if we make sure that the Zs as measured with our meters is not more than .8 of the "calculated" "design" figure, we can be sure all will be well when the cable IS at operating temperature.
I think it should make clear on the forms whether they are asking for the Zs as calculated and corrected to the cable max operating temperature, OR whether they want the MEASURED value at normal ambient temperature..
So, everyone is right, for all i know they might have changed the wording of the question on different age forms..
john..