Ok heres goes, i'll get right to the point.
Changed a CU and plan to use it for my Elecsa assessment.
Everything checks out fine with regard testing and all to current regs, apart from...
...garage spurred from downstair RFC:O, so have now made the spur into a radial protected by a 16amp RCBO. (Not perfect, but miles safer than before and you guessed it, the customer will not pay a garage CU and new supply).
So my main worry is as the earthing is tnc-s, am I likely to get a big red cross from the assessor on the day, as I've essentially exported the earth in the garage.
(The garage does not have any extraneous conductive part by the way.) ut the kettle on
Thanks for your input people