toolsparky
Junior Member
- Joined
- Sep 16, 2012
- Messages
- 2
- Reaction score
- 0
Hi. Do the regs state that only a 4 Pin socket outlet, should be used with 3 phase and earth cable and never a 5 pin??
Today a contractor turned up at our engineering factory with a Space age £80,000 German Laser welding machine to do some specialised on site welding. He plugged his 16 amp 5 pin socket into our wall socket, tried to operate his machine and it Juddered like mad and blew an internal 6 amp MCB!
I was asked to check out the supply to the socket and found there is no Neutral wire to the Neutral pin. I then found an alternative socket that has 3 phase, neutral and earth supply, but as soon as the machine was connected to this supply (even though the welders isolator was turned off), the 6 amp Internal MCB would blow again.
In the past the socket has just been used for a Balanced Neutral Motorised polishing machine, but I guess this Welder, having electronics galore and 230v internal circuits may have been damaged in some way, by the lack of neutral. What implications does the lack of a Neutral have for a machine of this type?
The socket was fitted several years ago by one company and there have been 2 PIR's since from different electrical companies that have not flagged up a problem with this socket or the fact that maybe it should have been 4 pin rather than 5.
Obviously the contractor with the welder isnt happy that he has potentially very expensive repairs to face and is trying to blame the company I work for, even though we did our bit with regards to regular PIR's.
You would think that a sophisticated machine like that would have some kind of protective circuitry in case of a floating Neutral. Also it was strange that it tripped the internal MCB even though the Machines isolator was off!
Any comments or advice greatly appreciated
Today a contractor turned up at our engineering factory with a Space age £80,000 German Laser welding machine to do some specialised on site welding. He plugged his 16 amp 5 pin socket into our wall socket, tried to operate his machine and it Juddered like mad and blew an internal 6 amp MCB!
I was asked to check out the supply to the socket and found there is no Neutral wire to the Neutral pin. I then found an alternative socket that has 3 phase, neutral and earth supply, but as soon as the machine was connected to this supply (even though the welders isolator was turned off), the 6 amp Internal MCB would blow again.
In the past the socket has just been used for a Balanced Neutral Motorised polishing machine, but I guess this Welder, having electronics galore and 230v internal circuits may have been damaged in some way, by the lack of neutral. What implications does the lack of a Neutral have for a machine of this type?
The socket was fitted several years ago by one company and there have been 2 PIR's since from different electrical companies that have not flagged up a problem with this socket or the fact that maybe it should have been 4 pin rather than 5.
Obviously the contractor with the welder isnt happy that he has potentially very expensive repairs to face and is trying to blame the company I work for, even though we did our bit with regards to regular PIR's.
You would think that a sophisticated machine like that would have some kind of protective circuitry in case of a floating Neutral. Also it was strange that it tripped the internal MCB even though the Machines isolator was off!
Any comments or advice greatly appreciated