OK guys need some advice.
Scenario 400 Amp 3 Phase head supplying 3 Phase isolator, Supplying a 3 Phase buzz bar. All this is connected with 150mm Cable so no problems here, The issue is there is a 24 way 3 phase consumer unit connected directly to the buzz bar with 25mm Tails, Does the consumer unit need to have a 3 Phase MCB as the main switch I know it will only be 63 Amps, or a 100 Amp 3 Phase Fused Isolator to protect the 25 mm Tails from over current, or is it OK to connect to the Consumer Unit just with a 3 Phase Isolator as a main switch with no over current protection. The Consumer Unit is within 2 meter's of the head.
I think it needs over current protection but another electrician thinks an isolator would be OK.
Thanks in advance CJS
Scenario 400 Amp 3 Phase head supplying 3 Phase isolator, Supplying a 3 Phase buzz bar. All this is connected with 150mm Cable so no problems here, The issue is there is a 24 way 3 phase consumer unit connected directly to the buzz bar with 25mm Tails, Does the consumer unit need to have a 3 Phase MCB as the main switch I know it will only be 63 Amps, or a 100 Amp 3 Phase Fused Isolator to protect the 25 mm Tails from over current, or is it OK to connect to the Consumer Unit just with a 3 Phase Isolator as a main switch with no over current protection. The Consumer Unit is within 2 meter's of the head.