Went to a job to replace a water heater last week.
Its a TT system and the and a loop test on the circuit measured 269 ohms!
R1 + R2 was 0.67 ohms.
30mA RCD protecting cct.
Earth spike was existing but I decided to get longer/bigger rods to improve the reading.
2 rods screwed together and sunk to depth of about 1.8m only to hit solid rock. Could not better 269ohms.
Tried several more times up to 30m away and still no better.
Tried rods in parallel but no difference.
Customer says the site is built on rock.
I know 1667 ohms allowed on 30mA RCD but IEE say 200ohms max for Ra.
Where do I go from here?
Dave2