Hi
I have to decide on a circuit breaker for an air 22 KW, 3 phase 400V Air compressor.
Load current = P / (1.732 * V *PF) =22000 /(1.732*400*0.8)
= 39.69A
Imposing the 125% CB rule in accordance with NEC,
Current = 39.69*1.25 = 49.61A
Therefore a 50 A Type C CB is used.
These are my questions:
1. Do we have to include the PF if not given in the equipment datasheet for current calculation.
2. The 125% used above is according to NEC (American) standards. Do we have to include it while calculating CB size for UK installations following IEC Code.
3. Is this the right way to find the size of MCB?
Thank you in advance for your help.