Yes, I wonder if it is an attempt to clarify and distinguish? A true 2 pole RCBO might be unable to fit into a single module width given the space needed for arc blowouts etc. And there was a time when some really nasty single pole one module width RCBOs were made which only opened the phase - the neutral passed through for residual current sensing but was not switched, meaning an NE fault tripped open the L but NE fault could persist! SP+N indicates that the N is switched too unlike those earlier SP horrors. I guess in most single phase cases true overcurrent sensing in N isn't needed because if the N fault current differs from the L current then the RCD portion will trip and if the N fault current balances the L current but is too high then the MCB portion will trip?