Well.....
You got the three phases coming in yes??, they feed the isolator and then the 4 pole RCD.. So far so good..
You got the incoming neutral.. There does not have to be any means of isolating this [as long as it is not a TT supply OR domestic] but you can isolate it by means of the RCD which is better than nothing.. BUT, if it is TT, i would have thought that you would be wanting to isolate all live conductors at the one point, so a four pole isolator MIGHT be called for.
BUT and it is a rather big but.... It looks to me like you have the neutral bar connected to the backplate of the box, as is the Earth bar...
Now, i am only a welder, but this does not seem a very good idea to me soon as you load up any of the circuits the RCD will trip, AND if you lose the neutral, especially if you are on TT, switch any circuit on, and all exposed conductive parts will now be "live"
Also, what is the CSA of the cable you got leading from the RCD to the MCBS??? Is it sufficient for the total load as you got all the MCB's daisy chained together...
What earthing type you got???
john...