Hi All,
Just a question that's been eating away at me. I'm currently doing a new ring in a kitchen, earthing arrangements are TT, with a Ze of 21 ohms, so far so good. The cu is protected by a 250ma RCD main switch with the new ring to be put on an 32Amp, 30 ma RCBO.
Now the PFC is only 11 Amps, which is obviously not great enough to trip the overload protection in the event of a dead short, so how does it trip the RCD, is there a tiny imbalance at the instance the circuit moves from healthy to short? Or is there another rational explanation?