Fusing factors

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Dan007

Member
Joined
Aug 7, 2011
Messages
49
Reaction score
0
Hey guys, can someone point me in the right direction please, I'm looking for fusing factors for 60898 type B,C,D BS88 ect ect. I know 60898 type B is x5 but can't seem to find the others along with relevant max Zs equation. Any help appreciated :confused:

 
Hey guys, can someone point me in the right direction please, I'm looking for fusing factors for 60898 type B,C,D BS88 ect ect. I know 60898 type B is x5 but can't seem to find the others along with relevant max Zs equation. Any help appreciated :confused:
Hello Dan, You can get this from the time current graphs in appendix 3. Figs 3.4, 3.5, 3.6 are the types B C & D. If you look at the tables you can see they are x5, x10 & x20 as Andy said.

Doc H.

 
Thanks guys, I just checked my BRB as per your comments and can see it. Why they don't teach us during the 2330 level 3 I don't know, but I knew you guys wouldn't let me down :Salute

 
Hi Guys

Seeing as I am pretty old I thought I would jump in on this one.

Fusing factor is a historical throwback which is not explained in the book. Note that fusing factor is not in the definitions either.

Fusing factor was last used in the 14th edition, for real. It is a guarantee of popping a fuse or breaker with enough amps....

I shall give one example to clarify.

If you look a the time current curves for rewireable fuses on page 297 green book you will see that you need around double the current to blow a fuse. So that makes it 60A for a 30A and so on.

In the 14th, to guarantee a 'blow' the rewireable fuse was given a fusing factor of 3 so you needed 90A for a 30A unit.

Even more interesting, if you go back to the time/current curve on p297 and read off 90 A on a 30 A unit, it takes around 5 seconds for a disconnection so that is the origin of the 5 second discomnnection times that linger till today. :|

Now it is a long time ago but AFAICR the factors were....

Rewireable fuse 3

Cartridge fuse 2.4

Breaker 1.5 (no C and D in them far off halcyon days)

Finally, to close the lesson, looking at the above the 14th called the rewire-able 'coarse protection' and the rest 'close protection'

Regulation 533.1.1.2 basically states that you must not replace a cartridge unit ( close) with a rewire-able ( coarse) of the same rating as it will risk loop impedance compliance ....

I feel much better now for getting that off my chest:put the kettle on

Even though I have recently quit teaching, i cannot help myself:innocent

 
Dan; From the above Fusing Factor is actual fusing current divided by rating. I am surprised that you have not encountered it in training. My guys at level 2 know about it PDQ.

 
Hi everybody. Did not cach the point. Fusing Factor. It means, when the Fuse (in Automatic Switch) will react to overloading. Well. It'll happen, when the rating current is equal 1,13*Inom. In this case it ll happen during 1 h. (for the aut. switches up to 50A, and during 2h-from 63A). And if the current is 1,4*Inom-the fuse will react during > 1h (>2h for =>63A). But may be it is from another opera? Then I beg pardon. Berlioz.

 