Hi all
I am used to just doing domestic, but I've been asked to supply & install 4 hand driers in our local village hall. One of them I might be able to spur into an existing socket (I have to check first).
The other three I thought I would put on their own circuit, 4mm radial, on a 20A rcbo. The length of run would be about 28mts. Enclosed in either trunking or conduit.
The driers I've seen are about 2.5kw each.
Would diversity come into play on this? And do you think I'm going overboard with a 4mm cable?
Anyone recommend any driers?
Thanks
Malc