im a time serverd spark and this has been ticking through my head for a while now, as we have said a tt system relies on the rcd giving protection where the zs is too high.
saying this is unacceptable for tncs but is ok for tt seems hard to understand. now the 17th ed is in force and most boards have rcds covering all circuits the question has to be asked do we need to "worry" about zs as much. when i say this i mean should the regs be changed to allow a ball park for tncs e.g within x% of the ze. a type d 32 amp 60898 has a very low zs of .375 ohms. it does not take a long circuit to exceed this.
our nic guy pointed out a good case he came across the other day where the ka on a tt system was very low. so even on short circuit the device would not trip as there was not the current available to do so.
andy
im a time serverd spark and this has been ticking through my head for a while now, as we have said a tt system relies on the rcd giving protection where the zs is too high.
saying this is unacceptable for tncs but is ok for tt seems hard to understand. now the 17th ed is in force and most boards have rcds covering all circuits the question has to be asked do we need to "worry" about zs as much. when i say this i mean should the regs be changed to allow a ball park for tncs e.g within x% of the ze. a type d 32 amp 60898 has a very low zs of .375 ohms. it does not take a long circuit to exceed this.