Hello folks - cheers for reading and responding (if you do).
consider a main distribution board (DB) which has a distribution circuit; the circuit is to a 2nd final circuit DB that has a 30mA 40A rcd as its main incoming switch/protective device.
insulation testing (500v, using 3 tests: n-cpc, l-cpc, l-n) the main DB first as a whole (inc. the distrib circuit to DB2), is it likely to damage the rcd on DB2 (fed by the distrib circuit) if the rcd on DB2 is 'open'?
what is the 'best practise' in this scenario for the test?
i would say best to test main DB as a whole with protective device for distrib circuit to DB2 'open'. Then test distrib circuit separately by disconnecting at RCD-end on DB2 and connecting insulation res. tester at that end?
cheers for any views
best wishes all
PW