As EE rightly said, you need to disconnect all loads to get accurate readings. If it is impractical to do this then I would write a note in the limitations section saying something along the lines of "impractical to disconnect each emergency light fitting therefore 500v IR test omitted".I'm getting 0.11meg on live conductors to earth on a circuit of 25 em lights. I take it this is due to the battery packs and pcb's? Am I right? How would you get round this for a periodic? Thanks
I thought thats what he was doing which suggests he has something like 2mA leaking to earth on that circuit.Don't you just connect live and neutral together, and test between them and earth?