Is my PV setup safe? Should my Inverter be grounded?
SolarLover
May 3, 2022
19
3
Hi
I have a new on-grid system of:
17 x Q Cells Peak Duo Black ML-G9 380w Panels (6.46 kWh array) split over 2 strings 10 & 7
4 x Growatt PowerAmp ML33RTA 3.3 kWh batteries (13.2 kWh)
1 x Growatt SPH3000 6.6 kWh Inverter
My inverter is not grounded & I’ve checked with my installer and they say the Inverter does not need grounding; whereas the Growatt manual says it does!
They say “grounding the PV array this isn’t needed unless we are installing on a erroneous roofing material, we use that earthing point on the inverter to bond the 6.5kw batteries but there is no point available on the 3.3 kw batteries. The battery storage is 50 volts low voltage”
Our panels are on a tiled roof with inverter & batteries inside garage.
Is this correct?
Thanks in advance
binky
eco warrior......™
May 7, 2008
11,991
627
Sunny Plymouth
We don't generally ground (earth) the array on the roof, but do generally bond the battery cases to the inverter, which in turn has an earth connection to the circuit it's connected to. I've not fitted Growatt, so maybe what I have fitted is different.
SolarLover
May 3, 2022
19
3
Thanks for the reply
I found this in the Growatt SPH3000 manual that concerned me
binky
eco warrior......™
May 7, 2008
11,991
627
Sunny Plymouth
Yep, big bonding terminal, battery packs should have something similar. I've never been completely convinced of the need to bond, but if the manual says it should be done, it should be done.
Gian
Feb 4, 2021
141
28
Our of interest should the panels and rail be bonded and would it not be good practice to run a bond from arrays to inverter to allow test equipment like the seaward pv150 to connect up to test ground faults issues
binky
eco warrior......™
May 7, 2008
11,991
627
Sunny Plymouth
No, not necessary unless you have AC on the roof ie microinverters on a TN-C-S earthing system.
I've always been interested how inverters or the seaward test gear detect earth leakage without a bond, but they do.
Gian
Feb 4, 2021
141
28
I simply run an earth cable down on all installs now. I was advised by an expert.
binky
eco warrior......™
May 7, 2008
11,991
627
Sunny Plymouth
but then you are making a good attraction for lightning ;).
What was his reasoning for this? You could be, potentially, be introducing DC fault of 300/400V onto the earthing for the property without ADS for the DC side, even if the inverter detects the fault and stalls the DC side, 'if it's daylight, it's live'
Gian
Feb 4, 2021
141
28
It's placed in an IP rated box and only used for test purpose to save getting ladders out to connect when testing