davetheglitz
Electrician
Just a few thoughts on the dreaded earthing systems - can anyone see any problems with this?
TNCS - generally hated as if the neutral is lost any load in the circuit routes the live back to the earth terminal making every metal object live. The RCD will have no effect on this.
TT - hated by some as if there is a N-E fault on the system the return current to the RCD is shunted by the earth rod impedance. Will not therefore trip correctly in fault conditions - but will trip when the imbalance is greater than 30ma - e.g. current taken 30A - 30mA shunted to earth via rod - hence trip.
Thought - add an earth rod to a TNCS system - see attached diagram.
If neutral is lost at prior to the RCD and a fault occurs after the RCD then RCD will trip as >30mA taken via the earth rod - removes objection to TNCS
If N-E fault occurs after the CU current is shunted across the RCD - approx half flowing through the RCD, half across it. Any small appliance in circuit (>60mA) would cause a trip- so hazard is identified before any fault can cause injury - removes objection to the TT system.
Arguably this is mixing earthing systems - but in reality I can't see what the difference is with this and bonding to a metal pipe which goes to ground.
Overall - I think that the TNCS is probably a better earthing system than TT provided it is all RCD protected and any bonding provides a route to ground.
Any thoughts?
TNCS - generally hated as if the neutral is lost any load in the circuit routes the live back to the earth terminal making every metal object live. The RCD will have no effect on this.
TT - hated by some as if there is a N-E fault on the system the return current to the RCD is shunted by the earth rod impedance. Will not therefore trip correctly in fault conditions - but will trip when the imbalance is greater than 30ma - e.g. current taken 30A - 30mA shunted to earth via rod - hence trip.
Thought - add an earth rod to a TNCS system - see attached diagram.
If neutral is lost at prior to the RCD and a fault occurs after the RCD then RCD will trip as >30mA taken via the earth rod - removes objection to TNCS
If N-E fault occurs after the CU current is shunted across the RCD - approx half flowing through the RCD, half across it. Any small appliance in circuit (>60mA) would cause a trip- so hazard is identified before any fault can cause injury - removes objection to the TT system.
Arguably this is mixing earthing systems - but in reality I can't see what the difference is with this and bonding to a metal pipe which goes to ground.
Overall - I think that the TNCS is probably a better earthing system than TT provided it is all RCD protected and any bonding provides a route to ground.
Any thoughts?