NOTICE: THIS IS SOMEWHAT DANGEROUS IF YOUR NOT FULLY AWARE OF WHAT YOUR DOING. DONT TRY IT AT HOME (even i went to my workshop to try this)
following KME's thread, here's some experiments replicating his problem / results etc
the 4 way extension is fed from a TT suppply (L&N taken from TNS supply, earth connected directly to a rod, 203 ohms).
the multimeter is connected between the earth rod & the TNS earth so you can see exactly what voltage the rod is at
here's the setup as normal. neons are not as clear in the pic as i thought they would be. in this, all 3 lights are lit (polarity correct). megger also says polarity correct
KME said there was a 13 ohm fault L-E. my substitue is a 2KW heater (around 30 ohm) wired between live & earth (grey plug) not quite 13 ohm, but its close enough, and i couldnt be bothered altering the wiring in another heater to get it closer to 13 ohm.
also, fluke T-140 did buzz to warn of live conductor when it touched either live or earth.
dont own a neon tester so couldnt check that (sorry steps!)
not too clear, but plug in tester is saying L&N reversed. although the middle neon was very dimly lit.
the TT 'earth' is now over 200V compared to the TNS earth
and finally
fluke T-140 was hung in the air by a live conductor. on its own, it didnt warn of anything live.
but as soon as any part of the tester (body, flex, other probe (not tip) came into contact with anything else (me, me with insulated gloves, concrete floor, flex of live conductor it was hanging from etc), it did warn it was live.
following KME's thread, here's some experiments replicating his problem / results etc
the 4 way extension is fed from a TT suppply (L&N taken from TNS supply, earth connected directly to a rod, 203 ohms).
the multimeter is connected between the earth rod & the TNS earth so you can see exactly what voltage the rod is at
here's the setup as normal. neons are not as clear in the pic as i thought they would be. in this, all 3 lights are lit (polarity correct). megger also says polarity correct
KME said there was a 13 ohm fault L-E. my substitue is a 2KW heater (around 30 ohm) wired between live & earth (grey plug) not quite 13 ohm, but its close enough, and i couldnt be bothered altering the wiring in another heater to get it closer to 13 ohm.
also, fluke T-140 did buzz to warn of live conductor when it touched either live or earth.
dont own a neon tester so couldnt check that (sorry steps!)
not too clear, but plug in tester is saying L&N reversed. although the middle neon was very dimly lit.
the TT 'earth' is now over 200V compared to the TNS earth
and finally
looks like you were rightAndy,It has a path trust me!
IT may be you, it may be something else, but it has a path!
You need to think about Op Amps and the gain that can be achieved in analogue electronics with say a Darlington pair?...
fluke T-140 was hung in the air by a live conductor. on its own, it didnt warn of anything live.
but as soon as any part of the tester (body, flex, other probe (not tip) came into contact with anything else (me, me with insulated gloves, concrete floor, flex of live conductor it was hanging from etc), it did warn it was live.